Further to my previous thread on the design of concrete tanks storing hot water, I have a query relating to CL.1.2 'Field of application' of BS 8007 which states:
'This British Standard applies particularly to UK conditions, and although the principles are applicable to design in other parts of the world, the designer should take account of local conditions, particularly variations in climate and the possibility of earthquakes, which have not been considered for UK conditions. Consideration has been given to the storage of liquids at ambient temperatures or at temperatures up to approximately 35 °C such as are found in swimming pools and industrial structures. Recommendations are given for structures in aggressive soils and for structures in areas liable to settlement and subsidence. No recommendations have been made for the effect of any dynamic forces nor for the effect of ice formation on the structure, and the designer should refer to specialist literature for information.'
I'm particularly interested in the text in bold. Does this mean that if the water is less than 35°C then I dont need to consider thermally induced stresses. I cant find any further info on this in the code. I havent been involved with the design of a swimming pool before but have seen design examples were there has been no mention of thermally induced stresses.
The tank i'm designing will have water at 60°C, but we intend to insulation and line the inside of the tank to reduce the temperature of the inner concrete faces to 30°C. The tank is buried and the outside faces of the concrete will be at approx. 10°C.
Analysis shows that this lower thermal gradient through the concrete in combination with other loads still provides dominant bending moments in the concrete. Can these thermal effects be ignored?
Thoughts from everyone welcome and dont need to be directly related to BS 8007.
Thanks
'This British Standard applies particularly to UK conditions, and although the principles are applicable to design in other parts of the world, the designer should take account of local conditions, particularly variations in climate and the possibility of earthquakes, which have not been considered for UK conditions. Consideration has been given to the storage of liquids at ambient temperatures or at temperatures up to approximately 35 °C such as are found in swimming pools and industrial structures. Recommendations are given for structures in aggressive soils and for structures in areas liable to settlement and subsidence. No recommendations have been made for the effect of any dynamic forces nor for the effect of ice formation on the structure, and the designer should refer to specialist literature for information.'
I'm particularly interested in the text in bold. Does this mean that if the water is less than 35°C then I dont need to consider thermally induced stresses. I cant find any further info on this in the code. I havent been involved with the design of a swimming pool before but have seen design examples were there has been no mention of thermally induced stresses.
The tank i'm designing will have water at 60°C, but we intend to insulation and line the inside of the tank to reduce the temperature of the inner concrete faces to 30°C. The tank is buried and the outside faces of the concrete will be at approx. 10°C.
Analysis shows that this lower thermal gradient through the concrete in combination with other loads still provides dominant bending moments in the concrete. Can these thermal effects be ignored?
Thoughts from everyone welcome and dont need to be directly related to BS 8007.
Thanks