I have an interesting situation. A contractor poured a concrete tank that I designed (48' dia x 16' tall). The walls are 12" thick and have two layers of vertical bars and hoops. During the initial water test, there were a lot of leaks. The photos of the leaking areas were near the bottom of the tank, and they appeared to have been patched. I was concerned that the concrete had not been properly vibrated and hired a testing agency to perform GPR testing. They located some void areas; however they obtained more concerning data regarding the cover over the rebar. The cover for the vertical bars varied from 1/2" to 6 1/2" (2" was specified).
As the EOR, do I even allow the option for a coating to provide long term protection for the bars? I checked the impact of the new "d" and this is not a structural problem.