It all depends on the flexural characteristics of you dynamic equipment foundation.
In other words, it depends on if it’s a rigid block type or flexural table-top type foundation.
If it’s a rigid block type foundation, you are OK and the impact of reduced concrete modulus Ec caused by reduced fc' is minimum.
If it’s a flexural table-top type foundation, you are in big trouble as it might change the foundation’s dynamic characteristics such as natural frequency etc significantly, and you have to plug-in the new static modulus of elasticity as per ACI 318-11 8.5.1 Ec=57000*SQRT( fc' ), or use revised dynamic modulus of elasticity as per ACI 351.3R-R2011 4.4.1.2 and re-check pretty much everything.
From ACI 351.3R-R2011 Foundations for Dynamic Equipment Page 45
4.4.1.2 Dynamic modulus of elasticity—The dynamic modulus of elasticity is stiffer than the static modulus, although not in any simple form. [red]Established relationships suggest that the ratio of dynamic to static modulus can vary from 1.1 to 1.6, with significant variation with age and strength [/red]. In practice, engineers treat this strain-rate effect differently. In some firms, engineers perform calculations using the higher dynamic modulus while other firms and engineers consider the difference unimportant and use the static modulus from ACI 318. [red]The distinction is more important for elevated tabletop-type foundations where the frame action of the structure is stiffer if a dynamic modulus is used. The difference can also be important in compressor foundations where the stiffness of the machine frame must be evaluated against the stiffness of the concrete structure. For simple, block-type foundations, the concrete modulus of elasticity has no real effect on the design. [/red]
If the low strength concrete applies to you concrete pile as well, it will also affect you as it impacts the foundation’s damping coefficient C and spring stiffness K. You may need to re-run your dynamic analysis with the revised K and C and re-check everything.
anchor bolt design per ACI 318-11 crane beam design