Don't count on them being from negative moment, not that it probably matters much. We had one slab that developed these cracks and the owner had us look at it.
The 3rd Floor was occupied and had ant trails (little ridges in the sheet vinyl) above beams and girders at every column line.
An upper floor was shell space, so had practically no load above its self weight, and it had cracks in the same locations, mostly small, but some pretty good size. We had seen these before, so provided #3@12 top, IIRC. That did a heck of a lot of good, LOL.
I figured these were from negative moment, but one of the older guys pointed out that there was no negative moment in the slab from the slab weight because it cured in that position--duh.
He said that the cracks simply form there because that's where the slab is thinnest and the studs provide stress risers, almost like the perforated edge of a paper designed to be torn out. There's also lots of restraint against shrinkage and the slab was probably 150' long. I had to think about it a while, but I'm sure that's right.
Unless you have a shored system or some serious superimposed loads, I have serious doubts if your cracks are from negative moment. Not sure that it matters now--they're there.
That being typed, I did cause negative moment cracks in a lab specimen once. It was a 3-span footbridge. When I put 20 psf on two adjacent spans, it cracked over an interior support. I think it did not crack earlier from shrinkage because it was so stiff that it wasn't much thinner over the supports and because it had no studs. It also wasn't as restrained against shrinking as a real slab would be.