Concrete pouring for water tank wall height 5,5 m :
- No horizontal joints (not allowed by several codes)
- No problem to pour in one time ; depending on the method statement for concrete production + delivery + bucket lifting + pouring + vibrating, you have to plan vertical joints with stainless steel plate and hypalon seal in the centre and additionall rebars at the cold joint,
- The method statement will give you the detailed time schedule depending on available batching plant capacity and truck mixers (nb, capacity) and distance from production area to cosntruction site
- This time will impact the concrete mix design and may be impose to use a plasticizer and /or a set retarding admixture
- Trials mixes and tests are highly recommended to check concrete consistency (sump) as it will need proper vibration at 5 m depth
- Using tremi-pipes is recommended to limit at max 1,00 m the free drop height in order to avoid segregation
- Vibration is very important to avoid segregation and honeycomb defects, it shall be properly designed and organized,
- For a 500 mm thick wall, concrete temp should be monitored and formwork removal allowed when temperature difference between concrete surface and outisde becomes less than 20°C .