If you see non-symetrical shears instead of conical, that would be an indication of poor sample preparation (non-parallel surfaces), improper placement of the samples (off-center) or some testing machine problem.
We had historically had photos of all concrete block prism failure modes and found that the platen thickness were not great enough for larger size (12"x16" or greater top areas). Because of the lack of rigidity, the platen deformed and concentrated the loading. This ultimately lead to greater platen thickness for block prism testing to qualify for ASTM.
Dick