Concrete Creep due to Increased Load on a 12 year old floor 1

Status
Not open for further replies.

ajk1

Structural
Joined
Apr 22, 2011
Messages
1,791
Location
CA
If an increased load is applied to a concrete floor slab after the floor has been in use for 12 years or so, what is the creep factor that should be used to predict the additonal long term creep due to the additional load?

Can creep be essentailly ignored because the concrete is so old at the time of application of the additional load?
 
I think creep is timeless but I'm not certain.


(I don't think I've ever written a sentence like that)

 
ajk1,

There is a maturity effect that reduces the amount of creep as the time of loading is extended, but there will still be creep. According to the Australian code it would reduce by about 30-40% from loading at 7 days after about 1 year and then stay constant at that figure. But the reduction from 28 days to 1 year is only 10%.

So it depends on your starting point or starting assumption! If you are simply using code multipliers, you would not know!

Other than that JAE is correct.

If you look at your design codes creep data it should tell you.
 