In Canada, you can spec a concrete mix design or leave this option up to the suppler. Typical spec options are: type of construction, f'c, cement type, max w:c, max slump, aggregate size, air content, and admixtures. For your use:
[ul]
[li]I would assume the C40 is 40MPa;[/li]
[li]you would specify the type of cement powder to be used depending on the requirement (this can be left to the supplier);[/li]
[li]you can set the w:c to 0.4 max;[/li]
[li]you can set the slump equal to 75 to 100 max, depending on what you are doing;[/li]
[li]max aggregate size can be set to 40mm, or larger if you can use it;[/li]
[li]air content can be set to 5% to 7%, depending on what you are doing; and[/li]
[li]admixtures can include the normal ones plus you can add a hydrophobic one to reduce the permeability.[/li]
[/ul]
In addition:
[ul]
[li]you have to take care of any rebar coating systems;[/li]
[li]make sure you have adequate concrete cover;[/li]
[li]you need sufficient bar spacing to reduce cracking; and[/li]
[li]make sure you have adequate consolidation for a dense cocrete placement.[/li]
[/ul]
We would normally leave the mix design to the supplier. The supplier should provide you with their mix design so you can review it (or have a good geotekkie review. Suppliers are often reluctant to provide this because they consider it proprietary. Have this as a specification requirement).