dcStrucEng
Structural
- Feb 26, 2009
- 45
I have come across many threads on this site regarding concentrated loads on composite slabs. But I have a slightly different twist on things on which I am hoping to get opinions. I have reviewed the concentrated load example in various deck catalogs as well as reviewed the information in SDI’s Standard for Composite Steel Floor Deck Slabs. For my particular case, much is known about the existing composite slab because I have existing drawings. The one thing that I am not confident about is the concrete cover dimension over the welded wire reinforcement.
When analyzing the slab for a known concentrated load over a known contact surface area, the slab has enough capacity for strong axis moment, one-way shear, and punching shear. The only limit state in which capacity is exceeded is weak axis moment. I am hesitant to proceed with a slab strengthening remediation to the existing slab solely for this lone limit state not meeting the required demand.
If I were to assume zero welded wire fabric in the slab and analyzing the weak axis direction as plain concrete also does not provide sufficient capacity. The equations and notes in the deck catalog example and SDI Standard do not state that the distribution of the concentrated load in the directions parallel (W) and perpendicular (be) to the flutes vary with or without WWF. Although I agree that distribution steel helps.
So even if the weak axis moment demand exceeds capacity, how will this really impact the slab? If this causes the slab to crack parallel with the flutes, the slab will act even more like a one-way slab. Anyway, I’ve spent significant time pondering this issue and would appreciate any opinions/advice from others. Thanks in advance!
When analyzing the slab for a known concentrated load over a known contact surface area, the slab has enough capacity for strong axis moment, one-way shear, and punching shear. The only limit state in which capacity is exceeded is weak axis moment. I am hesitant to proceed with a slab strengthening remediation to the existing slab solely for this lone limit state not meeting the required demand.
If I were to assume zero welded wire fabric in the slab and analyzing the weak axis direction as plain concrete also does not provide sufficient capacity. The equations and notes in the deck catalog example and SDI Standard do not state that the distribution of the concentrated load in the directions parallel (W) and perpendicular (be) to the flutes vary with or without WWF. Although I agree that distribution steel helps.
So even if the weak axis moment demand exceeds capacity, how will this really impact the slab? If this causes the slab to crack parallel with the flutes, the slab will act even more like a one-way slab. Anyway, I’ve spent significant time pondering this issue and would appreciate any opinions/advice from others. Thanks in advance!