BSVBD
- Jul 23, 2015
- 463
The building i am working on requires remodeling such that i will have the base plates of new steel columns bearing on an existing 8" brick wall. Not yet at Demo stage, design-wise, we are assuming a 3-wythe thickness / layout / configuration of the existing wall.
I WILL have demo'd, as necessary, to install grouted concrete masonry bond beams on top of the existing clay brick, if necessary.
I have a 6" thick "Masonry Technical Manual", filled with "Technical Notes" for Brick and Concrete Masonry. The dates on most of the notes range from the 1960's through 1980's.
The seemingly most applicable table i could find says "Minimum Compressive Strength" of Clay Masonry Units, depending on the Grade (SW, MW or NW) is, (the lower of the three), 1,250 psi. A foot note states, "Many units have compressive strengths far greater than these required minimum."
Conservatively, 0.2f'm = 0.2 x 1,250 = 250 psi. I can deal with that!
However... is this reasonable? Other Tech Notes suggest much higher compressive strengths. I certainly want to be conservative, but, not unreasonable.
Any other thoughts to determine a safe, allowable compressive strength for existing brick manufactured around 1013?
Thank you!
Thank you!