CSA S16.1 has requirements for the deck and slab thickness...
The effective slab thickness is the lesser of .25*span, 16*the slab thickness + width of the beam, and 1/2 the span to the adjacent beam for beams with slabs on both sides.
There are also requirements for slab and deck and steel studs often requiring that the composite deck be used in an inverted manner to achieve sufficient concrete for studs.
As far as the point loads, there are requirements for distributing the shear connectors along the beam to roughly correspond to the shear force diagram. It is possible, for example, to have a composite beam with a single large point load, say, at third span.
Dik