Composite Beam Deflection 2

Status
Not open for further replies.

peinma

Structural
Joined
Oct 4, 2005
Messages
17
Location
US
The commentary in AISC 13th states that for realistic deflection calculations Ieff should be taken as 0.75*Iequiv. Does this mean multiply Ieff as calculated per Eq. C-I3-3 by 0.75? Does Iequiv = Ieff? Reference pages 16.1-308 to 16.1-309. There is also an option to apply the 0.75 factor in RAM Structural System v14.

Thanks.
 
Ieff = 0.75Iequiv where Iequiv is calculated per C-I3-3. In the first edition of the manual equation C-I3-3 was incorrectly labeled as Ieff.
 