Mr Histor (Electrical)(OP)8 Apr 23 05:25
" .... how can I use common Field E-Stop button for multiple motors? There are around 9 motors in the package which needs to be wired to one EStop at field. In Motor control center panel, all these 9 motors has individual DOL Starter circuits as attached. But now I would like to use a common E-Stop instead individual EStops. How Can I easily fix this issue? "
1. I noticed that there are numerous mistakes/errors to look into:
(a) L1, L2, L3 and N are reversed,
(b) All breakers Qxx shall be 3-pole. N-pole shall not be used for L3,
(c) All main contactors KMxx shall be 3-pole. Auxiliary contact shall not be used for L3,
(d) M2 is wrong. Should be M1 etc., also on the others,
(e) to add a Stop push-button in the MCC instead of using E-stop as a Stop,
(f) there are other errors ........
2. There are E-stop push-button on the market that can stack/add on more contact block with NC contacts.
2.1 Replace the existing E-stops in the MCC by the field single E-stop push-button NC contact....
Che Kuan Yau (Singapore).