I'm coordinating an electrical system where a 1600 amp breaker controls six (6) K-rated dry-type transformers.
To simplify the problem, I'll say they are all 150 kVA.
The full-load amperage on a 150 kVA xf at 480 Volts ~ 180 amps. The inrush for a K-13 transformer can be as much as 15X.
Using a range of inrush from 8-15X, that could equate to (8*180*6) 8640 amps - (12*180*6) = 12960 amps.
The 1600-amp panelboard breaker has a maximum Instantaneous setting of 6X, or 9600 amps.
The transformers are separated physically by probably 15-20 feet of cable, as they are located on different floors.
I'm trying to dispositon this one way or the other - that the breaker trips on inrush or it doesn't, but I can't find any supporting data showing the cumulative effect of multi-transformer energization.
In a perfect world, I would set the instantaneous to accommodate the inrush at the 15X level (provided the system had the capacity), but my breaker wont allow it.
Can anyone comment on inrush for multiple transformers?
I think the physical layout of the building, with separation between devices, may prevent them all from inrushing together, but I can't find any data on that.
Thanks for any comments,.
John M
To simplify the problem, I'll say they are all 150 kVA.
The full-load amperage on a 150 kVA xf at 480 Volts ~ 180 amps. The inrush for a K-13 transformer can be as much as 15X.
Using a range of inrush from 8-15X, that could equate to (8*180*6) 8640 amps - (12*180*6) = 12960 amps.
The 1600-amp panelboard breaker has a maximum Instantaneous setting of 6X, or 9600 amps.
The transformers are separated physically by probably 15-20 feet of cable, as they are located on different floors.
I'm trying to dispositon this one way or the other - that the breaker trips on inrush or it doesn't, but I can't find any supporting data showing the cumulative effect of multi-transformer energization.
In a perfect world, I would set the instantaneous to accommodate the inrush at the 15X level (provided the system had the capacity), but my breaker wont allow it.
Can anyone comment on inrush for multiple transformers?
I think the physical layout of the building, with separation between devices, may prevent them all from inrushing together, but I can't find any data on that.
Thanks for any comments,.
John M