Interesting insight.
For this instance, current slab 6", new concrete 6" and localized to the anchor, with sufficient edge distance for the load. And the new would actually have a hairpin around the anchor to tie to and adjacent raised slab (but obstructed above). Im sure a detail would help here..
I suppose they should be bonded together with some weldcrete
By mobilize do you mean failure?
So I put together a sort of generic detail for this. Hope this helps. Obvs the anchor will be connected to something else, but left that out, just considering the embedment into the two differnt potions.
Currently thinking (A) considered as one slab (B) Considered as two slab with tension load distributed to representative embedment length or (B) considered separately with specific embedment depths, then sum capacities and apply a reduction factor of say 0.75
For reference:
I actually found a thread considering the combination of post-installed & cast in (though in a very different way) on EngTips (
One reply referenced the Sept 2021 issue of StructureMag (
- again not completely relevant, but related and interesting