To thicken the slab in the vicinity of the columns with post tensioning may be counter productive for moments (assuming the thickening portion goes down to yield a flat slab. For a 3 storey building on a granitic material, albeit fractured, are your footings large enough to require a full post-tensioned slab for bearing?
I've not ever used them for column rebar, but I often use 'Z' shaped dowels for slabs. They are embedded in a keyway and straightened after the keyway filler is stripped out. The bars sort of look like:
. ___________
. |_____
and straighten to look like:
. |
. |
. |
. |
. |
. |_____
(The browser formatting will likely really mess this up)
If you have small bars, you can try something like this.
Also, there's a corrugated galvanized tubing material (like a small diameter culvert) that can be inserted and the increased diameter enhances bond. The column dowel rebar could then be post-installed using an expanding or non-shrink type grout (used this for the odd precast project).