I have a project for a second story porch roof collapse. No surprise given every home in this area has severe deflection problems with either the upper level porch floor or roof.
In re-designing the porch, I have a setup with two exterior 6x6 posts that will set onto the existing brick piers ~8 from the home. I'll reinforce the 2nd level porch floor with a new LVL beam, since it's already deflecting and has a junk 2" post at midspan.
The posts will extend to the and roof level and support two 3-ply LVL beams that will tie back into the home at existing beam pockets. These beams will pick up 4 pre-engineered roof trusses spanning 25' each. With an end reaction of ~1.8 kips, I am wondering if this is an appropriate design.
The wall structure is ~12 thick with brick masonry veneer, ~3 5/8" and presumably 6"-8" wood studs. I don't believe that it is multi-wythe construction, but I was unable to verify this. If so, then I will use the City of Chicago porch design details for beam pockets.
My question is whether placing a reaction this large near the ends of the home is a good idea. I am unsure how they will frame the beams into the wall and be able to get positive bearing via the existing beam pockets. Can you only face mount the beams, since there is a ribbon board likly in place.
I was thinking that maybe running another 3-ply LVL header up high from post-to-post out front and then framing back to the house at 16" c/c would be a better way of picking up the roof.
If anyone has any ideas about what the likely construction of the exterior wall is, and whether I should try to support the roof continually across the face of the home instead of at only two locations, I thank you in advance.
It's possible that the 1.8 kips reaction is not that severe a load for an exterior wall, but I don't know if there are any defects that may reduce the capacity.
Thank you
I have a project for a second story porch roof collapse. No surprise given every home in this area has severe deflection problems with either the upper level porch floor or roof.
In re-designing the porch, I have a setup with two exterior 6x6 posts that will set onto the existing brick piers ~8 from the home. I'll reinforce the 2nd level porch floor with a new LVL beam, since it's already deflecting and has a junk 2" post at midspan.
The posts will extend to the and roof level and support two 3-ply LVL beams that will tie back into the home at existing beam pockets. These beams will pick up 4 pre-engineered roof trusses spanning 25' each. With an end reaction of ~1.8 kips, I am wondering if this is an appropriate design.
The wall structure is ~12 thick with brick masonry veneer, ~3 5/8" and presumably 6"-8" wood studs. I don't believe that it is multi-wythe construction, but I was unable to verify this. If so, then I will use the City of Chicago porch design details for beam pockets.
My question is whether placing a reaction this large near the ends of the home is a good idea. I am unsure how they will frame the beams into the wall and be able to get positive bearing via the existing beam pockets. Can you only face mount the beams, since there is a ribbon board likly in place.
I was thinking that maybe running another 3-ply LVL header up high from post-to-post out front and then framing back to the house at 16" c/c would be a better way of picking up the roof.
If anyone has any ideas about what the likely construction of the exterior wall is, and whether I should try to support the roof continually across the face of the home instead of at only two locations, I thank you in advance.
It's possible that the 1.8 kips reaction is not that severe a load for an exterior wall, but I don't know if there are any defects that may reduce the capacity.
Thank you