I have a situation that I would like some opinions on. A contractor had begun pouring a spread footing for a gravity column and run out of concrete. The next two concrete trucks were rejected, so the concrete that had already been poured into the foundation had hardened. The contractor had proceeded to pour the remaining portion of the foundation creating a cold joint at mid-depth of the footing. My question is what should I recommend as remediation?
The column is only a gravity column, therefore there are no concerns of lateral moments, only that created by the resisting soil pressure. Since there are no dowels between the two segments of concrete, shear friction based on ACI-318 cannot be attained. My thoughts were to determine the in-plane shear stress at the cold joint and have the contractor drill and epoxy reinforcement dowels required to resist that shear. Are there any other suggestions?
Thanks
The column is only a gravity column, therefore there are no concerns of lateral moments, only that created by the resisting soil pressure. Since there are no dowels between the two segments of concrete, shear friction based on ACI-318 cannot be attained. My thoughts were to determine the in-plane shear stress at the cold joint and have the contractor drill and epoxy reinforcement dowels required to resist that shear. Are there any other suggestions?