I could find no answer using the forum search, so sorry if I have overlooked a previous discussion. I am looking for some help determining the diaphragm strength of cold-formed steel framing with a steel sheet (NOT corrugated) shear member. AISI S213 allows a shear wall to be clad with 0.018" steel which provides a nominal strength of 485 plf or a 0.027" sheet which provides a nominal strength of 647 plf (assuming fastener spacings of 6"/12"). However, there are no tabulated diaphragm values for the same steel sheet thicknesses. Therefore, I thought I would calculate the shear resistance based on Principles of Mechanics per section B2 of AISI. This is where I am having problems. I am calculating the shear strength of the sheet steel per section C3.2.1 of the AISI design manual assuming transverse stiffeners. You can see in my attached example that a 20' long, 8' deep diaphragm sheathed with 14 GA steel yields a very low allowable shear capacity. The problem stems from the h/t value and the a/h limit of (260/(h/t))^2. Perhaps I am using the wrong values of "a" and "h" and the fastener spacing affects these values? Currently "h = diaphragm depth" and "a = joist spacing". Sheet edges will be blocked when orientation of the sheet would otherwise be unsupported. I am currently comparing the shear at the diaphragm ends, but what about the longitudinal shear between the sheet and the chords? I am currently ignoring that, but maybe the community thinks it should be addressed? If so, would my "a" and "h" values need to change because of the change in direction of the shear?
Something gives because:
A shearwall (cantilever beam) sheathed with 0.027" steel has an allowable wind shear load of 323.5 plf (2.0 safety factor) per the tabulated values of AISI S213 while a 2.8 times thicker sheet used in a diaphragm (simple span beam) has an allowable capacity 6.6 times weaker per my calculation.
Additional Info:
Once this is resolved, I will also incorporate this to be used in calculating headers sheathed with sheet steel on both sides. I already have a method of calculating the diaphragm deflection with the sheet steel by combining concepts of both the sheet steel shear wall deflection equation and the wood sheathed diaphragm deflection equations given by AISI S213-07. If you would like to see that, just let me know. I will not allow the aspect ratio to control when I use this method, rather I will allow the strength and deflection calculation to control.
Juston Fluckey, SE, PE, AWS CWI
Engineering Consultant
Something gives because:
A shearwall (cantilever beam) sheathed with 0.027" steel has an allowable wind shear load of 323.5 plf (2.0 safety factor) per the tabulated values of AISI S213 while a 2.8 times thicker sheet used in a diaphragm (simple span beam) has an allowable capacity 6.6 times weaker per my calculation.
Additional Info:
Once this is resolved, I will also incorporate this to be used in calculating headers sheathed with sheet steel on both sides. I already have a method of calculating the diaphragm deflection with the sheet steel by combining concepts of both the sheet steel shear wall deflection equation and the wood sheathed diaphragm deflection equations given by AISI S213-07. If you would like to see that, just let me know. I will not allow the aspect ratio to control when I use this method, rather I will allow the strength and deflection calculation to control.
Juston Fluckey, SE, PE, AWS CWI
Engineering Consultant