Old(er) plants used to implement what seemed good ideas at that time, name a few but not limited to: Plug valves (it was marketed as one of the best tight shut off valve), pressure seal (reduce some weight on piping compared to conventional B/B valve), Y-type globe valve (easier to operate/seal, etc.)
However, there are disclaimer in compensation for all of the above. Metal seated Plug valves usually lubricated hence periodical lubrication are required; pressure seal’s sealing plate/ring joint have fatigue lifetime and should be replaced after some years; and many others.
Please consider that this was the era where operator were generally allowed to be multi-tasking as well as have better sense of valve-ownership. Personal opinion, now we give those kind of tasks to subcontractor, external valve specialist, etc.
And throughout the years, it feels like we’re leaning to end user comfortable zone and change everything accordingly. My operator stop doing plug valves lubrication since 15++ years ago.
As long as there is no written feasibility report or risk analysis written from those days, it’s hard to justify what was inside our predecessors’ head when they select such valves. And can only compare both features apple to apple.
Metal seated lubricated plug valve vs metal seated ball valve:
Similarity:
Quarter turn vs quarter turn comparable travel time and actuator
Difference:
Lubricated every xy months vs no lubrication
Internal leakage: tighter (with lubricant) vs less tighter (ball valve normatively starts to worn out after xy cycles). End user start to accept that internal leakage is not top priority?
Usually port size 70% vs full bore.
Friction and actuator sizing??
Regards,
MR
All valves will last for years, except the ones that were poorly manufactured; are still wrongly operated and or were wrongly selected