I am working with a highly flammable gas that is in an enclosed system, normal operation will never have fumes and or vapors. The internal system, will be the pure flammable gas, with no air or oxgen, so it will always be above the UEL.
I am using mechanical ventilation to ensure if I have a ruptured line, that the gas concentration in the room will never approach 25% of the LEL which is 4%.
I have done calculations to show that this concentration will never exist if the ventilation is on. I plan on interlocking the supply valve to a positve flow sensor in the duct so it will not be on if there is no ventilation.
I am classifying the room as Class I Div II for the gas.
From what I can tell I should be almost able to argue that this is a general industrial situation, yet in past jobs, that had at least one instance of a similar situation, that facility had blow out panels on the buildings the flammables existed.
I have started reading NFPA codes again and am finding more relevant information, but I definately apprectiate any and all feedback.
Some other details, this room is in the USA and will be modular type construction, and as I am in design phase, It can be what ever best suits the application and code.
Its a production unit that will be servicing a larger oil based production rig that will have operations personell walking around the unit. That is why im worring about blow up panels to release sound and pressure waves and protect people both in and outside of this unit.