Hi all,
I have been asked to do a code evaluation for a conventionally framed residential roof (4:12) in Alberta Canada that has failed under snow load. The snow load was most likely at or just past the design load.
I am using the 1965 NBCC in the review. The code gives maximum rafter spans, say for example 11'10" for a 2x6. The rafters used were 2x6 spanning 15' to an unsupported ridge plate. The code also requires all structural members to safely support the design loads and prescribes the number/length of fasteners for each joint (rafter, ridge, ceiling joist, collar tie).
I have some general concerns with doing a code evaluation for a structure this old...but my specific question is whether it is appropriate to identify the rafter span as a code deficiency when the accepted practice of the day may have been to use collar ties to increase the effective span of the rafters. The collar ties where 24" below the ridge so that the 11' span could have been technically met if the collar ties were viewed as "supports".
It is clear from a modern analysis and literature review that the rafter set does not work (connection forces, unbalanced load at the ridge intersection, no fasteners at the rafter-to-1x6 ridge plate, etc) and this is also why the roof is failing and why the construction practice was abandoned. But is it inappropriate to use modern methods and knowledge to show that the structure did not meet code in this particular case?
Thanks to all in advance.
I have been asked to do a code evaluation for a conventionally framed residential roof (4:12) in Alberta Canada that has failed under snow load. The snow load was most likely at or just past the design load.
I am using the 1965 NBCC in the review. The code gives maximum rafter spans, say for example 11'10" for a 2x6. The rafters used were 2x6 spanning 15' to an unsupported ridge plate. The code also requires all structural members to safely support the design loads and prescribes the number/length of fasteners for each joint (rafter, ridge, ceiling joist, collar tie).
I have some general concerns with doing a code evaluation for a structure this old...but my specific question is whether it is appropriate to identify the rafter span as a code deficiency when the accepted practice of the day may have been to use collar ties to increase the effective span of the rafters. The collar ties where 24" below the ridge so that the 11' span could have been technically met if the collar ties were viewed as "supports".
It is clear from a modern analysis and literature review that the rafter set does not work (connection forces, unbalanced load at the ridge intersection, no fasteners at the rafter-to-1x6 ridge plate, etc) and this is also why the roof is failing and why the construction practice was abandoned. But is it inappropriate to use modern methods and knowledge to show that the structure did not meet code in this particular case?
Thanks to all in advance.