I am connecting RCP to CMP (15" or 18"). Besides pouring a concrete collar, is their another good way to make the connection and keep it soil tight / water tight?
I hadn't planned to, but client is requesting it. If you have information on a pre-fab connector, I would be interested in seeing it as I have not seen one yet.
I wish I had a sturdier answer for you CVG, but can only muster up this BS suggestion. Have you tried speaking with the trenchless people---maybe they have a sleeve, or a liner, or a coupling, etc? Nonetheless, I like LCrusier's idea, save my concern for the anode/battery action between the materials, potentially.
fine, except I can't bolt it to concrete pipe and this detail calls for a concrete collar which I would like to avoid. However, a spigot adapter might be useful along with a liberal application of bituminous mastic.
Check with Fernco,
CMP length pipe can end with a series of 4 non spiralled ribs that are rerolled after pipe forming, ensure this is specified to get a good sealing surface. note: CMP is not water tight.
A rubber coupling could connect to this effectively and connect to the RCP provided the sizes are correct.