A potential problem in one of our quick close valves was brought to my attention.
During normal operation, the actuator to the main valve is held closed by an 80 psi instrument air line. Upon loss of air, the main valve is meant to close quickly by way of a quick exhaust valve (QEV).
Please see the linked figures:
1. 2. 3. Further description of the QEV operation can be found here:
The potential problem seems to arise on cycling the main valve. There appears to be no vent to atmosphere, thus when the main valve loses air supply, the QEV vents air back into the actuator, equalizing the pressure and increasing the closing speed of the main valve (spring return closes the main valve).
When the main valve is opened again, that air remains in the line. Thus when the actuator closes, it has to overcome a greater pressure in the line than it did initially. For example, equalizing pressure occurs at 50 psi, then 50 psi must be overcome to close the actuator. On the next cycle, however, the air will still be in the exhaust line and the equalizing pressure when the air supply is removed will be higher, say 60 psi. Thus as the valve is cycled, it appears that it will eventually reach a state where the air supply pressure will not overcome the pressure in the exhaust line of the actuator.
If someone could explain how this closed loop system is supposed to work, I would appreciate it. I am not very experienced in closed-loop valve systems so I may be missing something. Thank you.
During normal operation, the actuator to the main valve is held closed by an 80 psi instrument air line. Upon loss of air, the main valve is meant to close quickly by way of a quick exhaust valve (QEV).
Please see the linked figures:
1. 2. 3. Further description of the QEV operation can be found here:
http://files.engineering.com/getfile.aspx?folder=6e71a13a-3b50-4c0f-b8d2-4cc10ca738c5&file=QEV.JPG).
The potential problem seems to arise on cycling the main valve. There appears to be no vent to atmosphere, thus when the main valve loses air supply, the QEV vents air back into the actuator, equalizing the pressure and increasing the closing speed of the main valve (spring return closes the main valve).
When the main valve is opened again, that air remains in the line. Thus when the actuator closes, it has to overcome a greater pressure in the line than it did initially. For example, equalizing pressure occurs at 50 psi, then 50 psi must be overcome to close the actuator. On the next cycle, however, the air will still be in the exhaust line and the equalizing pressure when the air supply is removed will be higher, say 60 psi. Thus as the valve is cycled, it appears that it will eventually reach a state where the air supply pressure will not overcome the pressure in the exhaust line of the actuator.
If someone could explain how this closed loop system is supposed to work, I would appreciate it. I am not very experienced in closed-loop valve systems so I may be missing something. Thank you.