Close Up Faults 1
Ashdgee
23
Hello all,
I am doing a relay settings study for 2 back up MV generators.In the relay manual for MiCom , they did mention the term Close-up falts.
Can someone tell me what is a close up fault (I have heard of close in/out faults)
Dear Mr. Ashdgee
Q. "...In the relay manual for ... , mention the term Close-up falts (fault)...".
A I am of the opinion that it is a translation "slip".
a) The terms [Far-from-generator short circuit] and [Near-to-generator short circuit] is used in IEC 60909
b) Refer to IEC 60909 for their definition and application in short circuit current calculation.
Che Kuan Yau (Singapore)
'Close-up' refers to fault close to the generator terminals.
Dear Mr. RRaghunath
Please advise which Standard viz. IEC, ANSI or publication etc., states " 'Close-up' refers to fault close to the generator terminals."
That would be in the MiCom relay manual. (Under the scope of "etc.")
Bill
"Why not the best?"
Jimmy Carter
I'd agree it's probably a translation thing; in my neck of the woods, "close-up" is a photography term, and a "close-up fault" would be something like the way a picture turns out where the distance between the camera and my face is so short that not only does distortion occur but individual nose-hairs can be counted... [blush]
'Close-in' is the term we use for faults close to the supply protective device, most typically a circuit breaker of some sort.
CR