dpc is probably right, but just in case, another issue may be the settings on the transfer switch. It sounds as if possibly the generator may be shutting down slightly prior to the switch transferring back, causing a slight loss of frequency. Switch-mode power supplies are sensitive to frequency drop and can cause problems, so most will shut down rather than allow corrupt data in microprocessors. Other hospital systems are probably on a UPS so they don't see it, but radiology is one of those not required to be on one. That may explain the clock phenomenon as well. I had this problem in hospital sterilization rooms, another non-critical area. When we went from relay logic to PLCs for the sterilizer controls, we had this come up a lot before we figured out what it was about.