Thanks Dik. You raise good points and I will try to answer them as best as I can. I feel that this really needs an enginer's engineer to solve the problem; it does not seem to be that the usual boiler plate problems/solutions are necessarily applicable here. Please note that my moniker of hope9010 and ajk1 are both me, just depends whether I send from the office or from home.
1. The wall is a crurved east wall of the buildng. The assembly is given on the architectural drawings as follows, and investiagtions to date have tended to confirm this:
Starting from the interior side, the wall above the level of the interior ceiling (i.e. where the majority of the brick spalling is located) is as follows:
- 1.5" of fibreglass insulation with foil backing vapour barrier
- 1/2" parging
- 4" brick interior wythe
- 1/2" vertical collar joint between wythes
- 4" brick exterior wythe
No breaks have been found in the vapour barrier, but a detailed inspection of all of it has not yet been made. I expect that the vapour barrier may not meet current standards. (It should not cost much to provide a vapour barrier meeting current standards).
The wall is curved in plan view, so that is most likely why it is brick and brick rather than brick and block.
The room is the main sanctuary of a synagogue, and is generally used only once a week, plus any weddings etc., but most of the time it is empty. The humidity in winter is low in the room, and in summer is high. Last weekend I measured the humidity in the room when the people were in it, as 27% and the air temperature as 74 deg. F at seat level. I don't know what it would have been in the ceiling space above.
The ceiling space is NOT a plenum. Ducts are used for supply and exhaust.
2. There is another east wall of the building with severe spalling near its top; that is the east wall of the top storey fan room. This wall construction is:
- 4" solid block interior wythe (no insulation, no vapour barrier)
- 1/2" vertical collar joint
- 4" brick
The fan room is not a high humidity area; I expect in the winter that it varies between 15% on a very cold day (minus 15 deg. C outside), to 30% when the outside temperature is near zero deg. C (32F).
3. Yes it is quite possible as you suggest that moisture is accumulating at the outer skin of the brick and freezing. But why should that be more prevalent on this building,than on other buildings?
4. There is no apparent damage to the wall. Near the top of the wall can be seen some mortar joints where there is a gap between the mortar and the brick, that perhaps could let rain penetrate to the vertical collar joint. There is a horizontal steel shelf angle located at about the interior ceiling level, that supports the exterior brick. If water gets into the collar joint, it would be blocked by this shelf angle. This might explain why the spalling predominates above the ceiling level.
5. There have been improvements to the building in terms of a new HVAC system but the spalling issue predates this by many many years. There has been no change to the windows, though an upgrade is scheduled. New roofing and increased insulation were installed about 3 years ago, but this was long after the brick spalling was already very severe and had gone thru one large repair of spalling.
6. One other point- the contractor who built it in 1965, thought that the bricks were very absorbent and applied a sealer, although this was not specified by the architect. I think that this was a bad thing to have done.
My own theory is:
a) the bricks have below average freeze-thaw durability properties (tests would be required to confirm this);
b) any moisture penetration of the wall is most probably mainly due to driving rain from the east;
c) due to poor freeze thaw characteristics, and perhaps exacerbated by the sealer applied to the wall in 1965, moisture penetration of the wall has caused spalling that might not be caused by moisture penetration of a wall built with more durable brick;
d) the spalling predominates above the ceiling line becasue moisture penetration is trapped in the collar joint by the supporting steel shelf angle;
d) the spalling predominates on the east wall because the driving rains come mainly with east winds in this city (as confirmed by the National Research Council);
e) I do not believe that the interior environment of the building is a significant source of moisture penetration to the wall in this building, although I agree that this is often the case in other buildings, particularly if they have hiugher humdity. The evidence to date does not support this theory for this building, in my opinion.
I am very interested in your further thoughts on this. Thanks for your help to-date.
No breaks in the