Class 1 Div 2 Enclosed HMI?

Status
Not open for further replies.

Louie2014

Electrical
Dec 17, 2013
1
I need to enclose and HMI& Controller inside an enclosure which is to reside in a Class 1 Div 2 environment. The HMI & Controller is not Class 1 Div 2. How can I do this and still maintain Class 1 Div 2? The HMI will not be mounted on the enclosure's lid but inside the enclosure such that the operator will need to open the box to view it.
 
Replies continue below

Recommended for you

OOPS. Put in an RFI - owner probably is overly conservative in the area classification. As you suspect, the only way that controller will meet Div-2 is to bolt it into an explosionproof box, and never open that box - just look at it thru the tiny [& dirty] window. Baring the above, it has to mount outside the classified area.
 