MUCOUR:
Regarding the API520 example 4.3.3.2 - this is my "take" on it:
Technically and in the real world I would agree with you that a balanced bellows valve is preferrable. If for no other reason than "how can they be sure 55 psig is REALLY CONSTANT!?! I would rather design for 0 to 55 psig variable back pressure.
That's point 1, now for point 2.
Again, technically a conventional valve is acceptable since (as you said) the 55 psig is constant, and 7.5 psig has been assumed to be the maximum variable without calculation (not a good practice except for preliminary sizing).
This is verified as follows: the total of built up back pressure (7.5 psi)plus the RANGE of constant back pressure (55-55 = 0) is 7.5 + 0 = 7.5 psi; and 7.5/75 is equivalent to 10% back pressure TOTAL.
This is OK since we have protected ourselves by setting the back-pressure derating factor to 0.88 (I used chart 30)in calculating the required orifice of 5.60 in2 (I actually get 5.63 in2 because my EXCEL sheet calculated C= 325 versus API's C = 326).
Point 3:
Again, in the real world, once I saw my design resulting in a back-pressure derating factor of < 1.0 ; that would normally trigger me to go back and select a balanced bellows valve.
Point 4:
If this was an existing valve, I would do it the way API has with the de-rating factor of 0.88.
Other Comments:
One thing I noticed that confuses me was that API in the Figure 30 footnotes implies (says?) this "correction factor should be used only in the sizing of conventional (non-balanced) pressure relief valves that have their spring setting adjusted to compensate for the superimposed back pressure". I wonder if I really believe that, I believe in fact that the chart is used for all conditions of back pressure so long as its a conventional valve in vapor and gas service.
The rules of thumb I have used for back-pressure factors before I know what manufacturer and model I have is as follows (I think I'm consistant with my previous notes):
For Liquids
kw = 1.0 if < 16% backpressure or for non-bellows type
valves
For Vapors. Gases:
kb = 1.0 if < 30% backpressure (TOTAL) for Bal Bellows or if
< 60% backpressure (CONSTANT, i.e.
SUPERIMPOSED) for a
Conventional Valve
Finally, my usual rule of thumb is to use a Balanced Bellows valve anytime TOTAL back-presssure is > 10%. So, here again, I would never do what API520 has done EXCEPT where the valve is existing. THEN, its a matter of engineering judgement regarding best practices and cost of re-work IMHO.
The more you learn, the less you are certain of.