tanaru
Electrical
- Feb 7, 2011
- 3
Hi,
I find out that one of the older wind farms from one of our customer has some serious issues with the circulating currents in the screens of the MV XLPE cables between the transformer and the MV cell. the values for the current are extremely high and they are having serious heating issues. We established that one of the issues was the way they laid the cables. the connection between the trensformer and the MV cell is done with three paralleled cable per phase and they laid them in RRR GGG BBB configuration instead of the RGB recommended formation. This determines variations between the cable length from 54 m on one of the phses to aprox 47 m on other phase.the cables are 33 kV XLPE of 500 mmp copper with 35 mmp copper screen and the distantce between phases is 25 cm.
The screens are both end bonded and the transformer is 110/33 kV of wye-wye configurations.
My question is that what other elements can drive those currents in the screens to be that high beside the laying configuration which is wrong?
Thank you,
Best regards,
I find out that one of the older wind farms from one of our customer has some serious issues with the circulating currents in the screens of the MV XLPE cables between the transformer and the MV cell. the values for the current are extremely high and they are having serious heating issues. We established that one of the issues was the way they laid the cables. the connection between the trensformer and the MV cell is done with three paralleled cable per phase and they laid them in RRR GGG BBB configuration instead of the RGB recommended formation. This determines variations between the cable length from 54 m on one of the phses to aprox 47 m on other phase.the cables are 33 kV XLPE of 500 mmp copper with 35 mmp copper screen and the distantce between phases is 25 cm.
The screens are both end bonded and the transformer is 110/33 kV of wye-wye configurations.
My question is that what other elements can drive those currents in the screens to be that high beside the laying configuration which is wrong?
Thank you,
Best regards,