Hi all:
I'm a bit confused about the approach for flagpole foundation designs. I designed a pole foundation based on IBC's straightforward approach in Section 1807 (Unconstrained round piers subject to lateral load). It was relatively narrow and deep (~2.25' wide and ~7.5' deep.) The contractor then prepared on-site an excavation for a premade "kit" which is wider and shallower with flared ends, which subsequently failed inspection. This off-the-shelf solution fails the IBC equation badly at the given dimensions (and doing some research it looks like flagpole foundations are often this odd shallow, nearly square "plug".) Are any of you familiar with how these foundations are justified? Since the steel for the kit is currently in the ground, the contractor wants to keep the shallow depth and widen the foundation to our satisfaction. Doing this with the pole-foundation equation gives huge diameters, and the only other method I'm familiar with is treating it as a bottom-supported spread footing with an eccentric load. I'm not aware of any design approach that combines ground-support with lateral moment resistance.
A constructably-reasonable circular spread footing results in there being negative soil pressure at the heel. So the actual pressure distribution would be circular with a "chord" missing in plan view. I don't have the time to relearn the calculus needed to do derive that from scratch. Are any of you familiar with a design approach or approximation that would give the actual toe pressure under those conditions?