patswfc
Structural
- Jul 5, 2005
- 164
I am currently looking at the design of 3 similar circular tanks with pinned connection at the base of the wall to existing slabs. They are approx. 7m tall with a working water level of 6m. The difference in the 3 tanks is the diameters which are 9.4m,12m and 14.5m.
According to the code, the allowable crack width at the base is 0.125mm as the walls are 300thk.
For early thermal effects to Ciria C660 (better known as drying shrinkage in the US) I calculate that the walls require 16s@125crs for the 0.125mm crack limit (includes use of GGBS in the mix, basalt aggregate, steel forms, etc to help reduce the thermal effects from hydration).
For ring tension the rebar needs to 20s@125crs for the 0.125mm crack limit.
Note, the tensile capacity of the concrete exceeds the max SLS ring tension by a factor of 3, however as cracks will have already formed due to early thermal effects then once the tanks are loaded, these cracks will get bigger due to the ring tension.
As both types of cracks will be vertical and through the full width of the concrete, I would think that both forms of cracking should be added together. If I do this then the required horizontal rebar increases significantly to 32s@125!
I find it difficult to believe that this much horizontal rebar is actually required, nor that others designing such tanks are providing this quantity of rebar.
I've found an example in a text, however this only checks the cracks widths for early thermal and loading separately, and doesnt combine these effects. Surely this isnt correct.
How do you consider crack widths in circular thanks?
Thanks
According to the code, the allowable crack width at the base is 0.125mm as the walls are 300thk.
For early thermal effects to Ciria C660 (better known as drying shrinkage in the US) I calculate that the walls require 16s@125crs for the 0.125mm crack limit (includes use of GGBS in the mix, basalt aggregate, steel forms, etc to help reduce the thermal effects from hydration).
For ring tension the rebar needs to 20s@125crs for the 0.125mm crack limit.
Note, the tensile capacity of the concrete exceeds the max SLS ring tension by a factor of 3, however as cracks will have already formed due to early thermal effects then once the tanks are loaded, these cracks will get bigger due to the ring tension.
As both types of cracks will be vertical and through the full width of the concrete, I would think that both forms of cracking should be added together. If I do this then the required horizontal rebar increases significantly to 32s@125!
I find it difficult to believe that this much horizontal rebar is actually required, nor that others designing such tanks are providing this quantity of rebar.
I've found an example in a text, however this only checks the cracks widths for early thermal and loading separately, and doesnt combine these effects. Surely this isnt correct.
How do you consider crack widths in circular thanks?
Thanks