If you (and the equipment) are in NEC land, then yes, NEC 450 is good. However, for small control transformers, the max fuse allowed is pretty high.
Unless you are inside of a panel - then you need to follow the panel listing, maybe look at UL508A
Unless you can't (follow the panel listing) - then probably NEC 409, NFPA 79.
Personally I like tight primary and secondary protection of control transformers. Smoked (overloaded or internally failed) control transformers have a nasty habit of burning up the insides of control panels - while not manageing to open the fuses. Nearly iratating.
Some likely would think it is way overkill, but I don't mind getting out a fuse TCC, and verifying the energization is within the fuse rating - especially if I had not done one before.
This way you could consider it engineering - not design by regulation, which usually is not a good idea.