Circuit Breaker - AC Generator 1

Status
Not open for further replies.

wpjo

Mechanical
Dec 16, 2005
2
On a portable AC generator, two individual 120V windings are feeding the two legs of a four prong (L14-30R) receptacle. Does a single circuit breaker on the neutral leg of the circuit provide the same protection as a circuit breaker on the hot legs? The neutral leg consists of the connected sides of the generator windings which feed the neutral side of the receptacle. Thanks.
 
Replies continue below

Recommended for you

The National Electrical code does not permit the use of a circuit breaker in the grounded (neutral) conductor unless it it a multipole breaker that also opens the ungrounded conductors.
Don
 
Think about it... You could have a severe over loading device plugged into that outlet that used the lines and no neutral... How would a neutral breaker prevent a melt down?
 