Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

choosing protection CT 1

Status
Not open for further replies.

Pafi

Electrical
Oct 21, 2002
40
Hello!
I wonder if someone can help me with tips/ document about choosing a suitable current transformer for a protection application - short-circuit close to generator - where the load current is 1000A, Ik'' = 30kA and Ipeak = 80kA. I need to choose according to IEC.
Thanks!
Pafi
 
Replies continue below

Recommended for you

This is an involved question. The primary criteria is to select CT's that do not saturate under fault conditions. If they are being used for current differential relaying, it is important for the CT's to have similar performance.

Have a look at some of the references under Power System Protection in faq238-1287.

Alan
----
"It’s always fun to do the impossible." - Walt Disney
 
Generally the relay manufacturers include CT sizing formula in the relay literaure. May be that should be helpful to start.
 
Hi Pafi.
Before few days we had thread on the topic.
Please see attached.
thread238-241062
You must choice CT also according to the relay's mnf. recommendation, for example, for the 87G, 87T protection ( as wrote Alan and Raghun).
Best Regards.
Slava
 
Very usefull tips!
thanks, I found what I was looking for.
pafi
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor