Hi COS,
The above two posters have it about right. For economy, it's good to pay attention to what the contactor manufacturers list as "standard" products though. At 1900 tons, you'll be looking at 1500+ amps, and standard motor starters don't go above 600 or 800 that I've seen.
At 4160 volts, you're down to 200 or less, but a hint here is that when you cross the 3300 volt mark, you're beginning to pay more of a premium for your contactor. Again, it's a line that the manufacturers have drawn due to UL differences, etc..., that makes the difference.
If you can get a 3300-volt motor, or even a 2400-volt, you should be in the "best economy" range for this size machine.
Let us know how it turns out!
Old Dave