Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JStephen on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Chiller Operation Performance

Status
Not open for further replies.

iken

Mechanical
Joined
May 13, 2003
Messages
151
Location
NZ
Hi,

I am invilved with a project that had a new air colled chiller installed. Since the install date, we have had no-end of faults (LP being the most common).

As it turns out, in the winter months there is very little internal heat load, so the chiller in turn sits idle. In fact, the chiller is only operational 4-5 months of the year (and vice versa - the boilers are manually isoalted in summer). What I would like to know is, would the Chiller just sitting there for say 6-7 months at a time doing nothing impact on it's reliabilty? Should there be some items undertaken at the season change (from Summer to Winter) to ensure the Chiller and parts will not deterorate over time, and is there any special tasks/items that should be done at season change again (winter to summer).

Many Thanks,
 
The chiller manufacturer should have a detailed maintenance and operations manual that covers these items. It's not the same for all chillers.
 
Pump may be started for few minutes once a week during the idle season - good for the pump's sealings.
Compressor carter's should be preheated to get rid of refrigerant in the oil - for some hours (better for a day) before starting the chiller in summer.
Etc.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top