chilled water systems
mechanicaldup
155
hi
where can I find design guide lines on chilled water systems?
I have a system with a supply temp of 6°C and return temp of 12°C. The system is cooling only.
What is the flow required per kW(cooling) estimated?
thks
Check ASHRAE book store.
Q = (m) (Cp) (Delta T)
With a 6 deg C delta T, the flow would be 2.22 USGPM/Ton or 0.14 L/s per Ton
HVAC68
Thks KRB
do you know of other usefull guides available from McQuay?
Where can I find tables to estimate the heatloss through the insulated chilled water piping network?
McQuay has some other manuals here:
I don't recall seeing any tables for heat loss, but 3E has a free software you can download to estimate heatloss for various pipe and insulation thickness. This is probably the best solution since you can input your specific data. You can generate a table from this software.
KRB