Chilled Water System Chemistry

Status
Not open for further replies.

KenRad

Mechanical
Joined
Sep 12, 2001
Messages
221
Location
US
Not sure if this is the right forum, but here goes.

I have a chilled water system which uses an atmospheric storage tank, so I guess you'd call it &quot;open-loop,&quot; although the system hardly loses or makes up any water at all. I had a mild steel corrosion coupon in the system, which after a month, showed <.01 mil/year loss. The way I understand it, the water is non-corrosive, and our water treatment program is working well. Are there any conditions where I still could have active corrosion of the steel piping in the system, and it not show up on the coupon? System circulation is good, so all the metal is seeing the same water.

---KenRad
 
Check the elbows and bends before control valves. In the past I had grave problems because of pitting.
 