Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Chilled Water Precision Air Handling Unit

Status
Not open for further replies.

schola

Mechanical
Apr 13, 2005
38
Dear sirs:

I've been estimating chilled water cooling coil "delta P", finding very diffferent values among common manufacturers ( DataAire (45 ft H2O), Liebert (10 ft), , APC(20 ft). for the similar equipment


Do you have a rough or practical standard value?

Regards,

schola
 
Replies continue below

Recommended for you

I would consider 10 mormal, 15 is getting high.

Take the "V" out of HVAC and you are left with a HAC(k) job.
 
5 psi or 10 ft is our usual allowance in absence of submittal data
 
The above replies are noraml ranges of DP. But the DP can be different depending on the Cv and the flow rate. You can use the : Q= Cv sqrt(DP) equation to calculate any DP and flow rate Q, if you know the Cv of the equipment.

Remember, the higher the DP, the higher you have to pay in energy for pumping the fluid through the equipment.
regards,
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor