I am dealing with the following situation on one of the projects we designed. During punch list, we noticed that contractor supported chilled water pipes to the bottom of a sloping roof beam (the beam span is perpendicular to the roof slope; the beams are 16 inches on center). The contractor bent the all-threaded rod and bolted it to the bottom flange.
The detail we supplied utilizes an angle that is bolted to three roof beam bottom flanges and the all-thread rods were to bolt to the angle and we called for beveled washer under the nuts.
I do not think what the contactor did is a good practice since it will introduce bending to the rod. Our company is being challenged by the contractor and owner to leave it as is.
As I look, all I can find is the 2004 RCSC specification section 6.1.1 which reads as follows:
“Sloping Surfaces: When the outer face of the joint has a slope that is greater than 1:20 with respect to a plane that is normal to the bolt axis, an ASTM F436 beveled washer shall be used to compensate for the lack of parallelism.”
I would like to get my hands on a documented reference (established one such as AISC manual or publication) so I can show them written documentation why they should change it. Does any one have more details or references?
Please feel free to comment on this situation as well.
Regards,
Lutfi
The detail we supplied utilizes an angle that is bolted to three roof beam bottom flanges and the all-thread rods were to bolt to the angle and we called for beveled washer under the nuts.
I do not think what the contactor did is a good practice since it will introduce bending to the rod. Our company is being challenged by the contractor and owner to leave it as is.
As I look, all I can find is the 2004 RCSC specification section 6.1.1 which reads as follows:
“Sloping Surfaces: When the outer face of the joint has a slope that is greater than 1:20 with respect to a plane that is normal to the bolt axis, an ASTM F436 beveled washer shall be used to compensate for the lack of parallelism.”
I would like to get my hands on a documented reference (established one such as AISC manual or publication) so I can show them written documentation why they should change it. Does any one have more details or references?
Please feel free to comment on this situation as well.