Chilled water buffer vessel sizing

Status
Not open for further replies.

Cooky

Mechanical
Jan 14, 2003
114
Does anyone have an equation that will calculate the required volume for a chilled water buffer vessel?

I use a 'rule of thumb' of 3 litres of fluid per kW of nett cooling, but I am after an equation that takes other variables into account. Such as number of chiller starts per hour, flow rates, desired temperature fluctuation.......

Thanks for your help.
 
Replies continue below

Recommended for you

See ASHRAE handbook for sizing expansion tanks. The tank can have a bladder, use compressed air or be open to the atm.
 
Sorry, very late reply to this and i guess you may not need it now but....

According to York: V=N x 60 x Z / 4.18dt

V= total system water content (Litres)
N= chillers first capacity step (kW)
Z= minimum allowable running time (min 5 mins)
dt= temp difference at minimum partload condition (say 2 deg C.).

This allows the chiller to operate smoothly at low load capacities and should provide sufficient thermal storage to give at least 5 mins operation after the machine has stopped running. This ensures the equipment doesn't keep stopping and starting at low load conditions.....by now, you probably already know all this!!
 