In essence they are "filling the bucket". Say you have a steady state fault current that results in tripping at 0.833 seconds and the relay process runs at 4 calculations per cycle. That means it's going to take 200 processor intervals to get to a trip, each interval adding .005 to the bucket. After 200 of those .005 results the sum is 1 and the trip is issued.
For varying currents, at each processor interval the relay accumulates some amount; take the trip time for the measured current and divide that into the length of the processor interval. Repeat until the sum gets to 1.