Hi guys, looking for some feedback on the design of temperature differential for chilled water systems. Here is what brought this up to my mind.
Lately, I have seen a lot of 15 degree chilled water systems on new building here in the NYC area. Previosly, most of the 15 degree systems I had seen where for cooling data centers and had a range of 45F to about 60F. Which is fine because there is not alot of humidity in a data center.
However, I have seen alot of chilled water systems designed for temperature ranges of 42 to 56 lately. And just recently I saw one designed for 42F to 60F, which is for a building with lots of laboratories.
The question would be as follows;
- Conventional thinking on design of chilled and hot water systems was that on hot water system you can tolerate a larger temp change because the water distribution temperature was so far away from the air temperature that you wouldnt notice much of a difference in average temp.
With chilled water system I always assumed that a 10 degree diff was used to keep the effective average coil temperature as low as possible to be able ensure that the air moving over it was cooled properly.
Also, most of these systems where I am seeing a high temp diff are variable flow primary pumping systems. I dont know if that makes a difference, but I figured I'd mention it. (on an unrelated topic, I personally feel that these larger temp differences in conjuction with variable flow primary can cause havok with chiller control systems since all of the evaporation of refrigerant happens in one spot, but I digress)
Here is what I am thinking on the design end.
I assume the point here is to make the chilled water system as energy efficient as possible so they start with the coils and increase the size of the coils to give the air more contact time and get it closer to the effective coil temp. From there the pumping system energy can be reduced because of using a higher temper differential.
My only thought here is having a chilled water setpoint on the chiller of only 42F does require a decent amount more energy than does a setpoint of 44F. But I assume when viewing the system as a whole this is less enegy intensive than the standard 10F differential.
If my understanding of anything here is incorrect please let me know where I am incorrect as this is the point of this post, to gain insight into the changes in designs for chilled water systems due to the use of high temp diffs and variable flow primary pumping.
If anything other information is needed please let me know.
Thanks in advance for any help.
Rob
Rob