I treated the "F" term as a target for iteration since it is the proportion of original mass remaining. I took the Bird equation as meaing "time to X% remaining". It didn't matter if I was starting at 1,000 psi or 100 psi, 1% remaining was still 1% (of a widely differing total mass).
Saloday's issue is really a boundary-condition issue. As long as the pressure near the leak is above the critical pressure required for choked flow, you'll have choked flow out the hole. In pipe above 10-inch, the friction drop from choked flow out a 2-inch blowdown is small enough to be negligible (i.e., at 100 psi the choked flow flowing out a 2-inch full-port ball valve is 8.9 MMCF/d which is about 12 psi/mile pressure drop in a 10-inch; at 30 psi the flow rate is down to 3 MMCF/d which is 2 psi-mile in 10-inch). If I use the pressure a mile from the blowdown to calculate the mass leaving, then at 100 psi I'm flowing 8.9 MMCF/d and at the valve I'm flowing 7.8 MMCF/d--this has always been close enought to tell me whether I needed to mobilize for a blowdown at 3:00 am or could let the guys sleep in till 4:00 am to have a line blown down by daylight.
David