Chain and Lock method to supervise a valve

Status
Not open for further replies.

Carlos Marsik

Mechanical
Joined
Jul 18, 2018
Messages
2
Location
CA
Good morning, I have several valves controlling the main water supply to domestic and fire protection services. Those valves, instead to have a supervisor reporting to the fire pànelpanel are protected with chain and lock. Is that accepted by NFPA_

Thank you.
 
Yes as long as you have a documented monthly and annual inspections as per NFPA 25. If this new construction the valves may need to be electrically supervised check with your local AHJ.

 
It varies around the country but in Georgia you will have to have it supervised electronically.
 
You say valves with a “S”

All of them may not have to be locked

Without seeing a pipe layout, hard to say.

We normally do electronic
 