The roof has a 96 PSF snow drift load.
The 10x162x12 gage roof purlins I have sized have a total reaction of 1,300 LBS.
How do you know if you need web stiffeners at the end bearing?
Following an SSMA Product Technical Information guide, the Web Crippling Load Tables show an Allowable Web Crippling Load of 2,396 LBS for 3.5" bearing. However, Note #1 says, "Only members with stiffened flanges are considered."
If that is the case, how, then, do I determine the allowable load for an UNstiffened member?
I have no problem specifying web stiffeners, but, I want to be efficient and wise. I don't want to stiffen the webs if not necessary.
Thank you!