270 Maintaining Acceptable Flow Rates for Centrifugal Pumps
271 General
All centrifugal pumps operate best when flow rate exceeds 40–50% of best efficiency flow. Deviation from this range can cause heat buildup, excessive vibration, damage, and failure. Figure 200-48 shows this operating range (minimum flow and maximum flow). Operation at or below minimum flow is especially critical for high speed pumps (such as Sundynes) because vibration can quickly cause gearbox damage.
Refer to Standard Drawing (GA-G1097-2) in the standard drawing section of this manual to determine the recommended minimum flows for specific pump selections. This drawing will usually be conservative. Several methods of pump control are used to prevent pump operation outside a preferred range: pressure control, flow control, and less commonly, electronic control based on electric power consumption. See Figure 200-49 on the page following and Figure 200-50 for schematics.
Pump controls circulate fluid from pump discharge back to a suction vessel or tank to maintain a minimum flow rate, or they impose backpressure on a pump to prevent runout. Runout is defined as operating beyond a pump's maximum recommended flow rate. Runout is most likely to be a problem when discharge lines are short (no friction loss) or when pumping into a system with low backpressure (e.g., an empty tank).
Operation of a centrifugal pump against a closed block valve can cause overheating, vibration, and eventual pump failure, and should be avoided for any significant length of time. It is normal operating procedure, however, to start centrifugal pumps with the discharge block valve “cracked open” (i.e. nearly closed) and the suction valve wide open. The discharge valve should then be gradually opened as discharge pressure increases. This promotes quick build-up of pressure and prevents cavitation, which can cause pump failures.
When using a recirculation bypass, never return fluid directly back to pump suction—this will cause swirling and heating problems which may raise vapor pressure and affect NPSHA. Instead, route the bypass line back to a tank, vessel, or heat exchanger.