Centravac
Mechanical
- Oct 15, 2003
- 13
one of the trane centrifugal chiller capacity is limited on high current (99%). condenser pressure is at 8.5 psig. Entering water temperature (condenser side) is 77 deg F. Also, inlet guide vanes are open 85 %. I suspect that there is oil in the evaporator tubes. Sight glass is to the top (cant see the upper level) but the evaporator refrigirant temp is 38.7 deg F which seems normal. Based on the privious years trends, I expect the load to be about 90 %.
.
Other running chiller with the same load is running at 90 % which is expected. Also, inlet guide vanes are open 67 %.
.
Any suggestions????
.
Other running chiller with the same load is running at 90 % which is expected. Also, inlet guide vanes are open 67 %.
.
Any suggestions????