- Oct 15, 2003
- 13
We have a issue with one of our chillers and I am hoping that someone can shed some light on it. One of our R11 Chiller is showing low condenser leaving water temperature and high Condenser approach. Here are the specs taken yesterday.
Condenser entering water temp = 34.6 F
Condenser leaving water temp = 68.8 F
Sat Evaporator Temp = 37.8 F
Evap rfgt pressure = -7.9 psig
Saturated Condenser temp = 94.1 F
Condenser Pressure = 6.6 psig
Condenser approach = 25.5
.
This Chiller has been out of service since 08/22/07 and we put it in service last week. All other indications are normal. Purge is 0 and unit seems to be working fine. We never had an issue with micro fouling, which can also cause this condition. Any thoughts?